You have a restricted orifice/metering device which is located on the liquid/high side of circuit... it's not low on refrigerant.
Need to recover refrigerant, replace orifice, pressure test with dry nitrogen, evacuate to 500 microns, charge to specs. You will be good to go
Note: you may also have a plugged evaporator coil which would cause low vapor psi. But seeing your high side is out of range and high leads to a common problem of a clogged orifice


You in the a/c field?



LOL


Sent from my iPhone using Tapatalk
 

04cr450

Active member
Joined
Aug 25, 2013
Messages
1,788
Reaction score
0
Location
harford county, maryland
More than likely u will get a fixed orifice, adjustable is more less of a universal device where you can adjust the liquid refrigerant capacity going into the orficice itself before entering the evaporator coil
 

jimdawg185

Active member
Joined
May 22, 2011
Messages
1,869
Reaction score
0
I just learned more about AC in this thread than the rest of my life combined.